Need help placing outdoor outlets on surfaces other than exterior structural walls.  I gather that a similar  issue has been addressed with regard to placing indoor outlets on cabinets (e.g., kitchen islands, etc.), but I do not think this is true with regard to placing waterproof GFCI outlets outdoors (e.g., on retainer walls, terrain walls, in or around outdoor kitchen areas, pergolas, etc.). However, this arises as an issue in many of my outdoor designs.   Can anyone please help me out here?.  Thanks very much in advance...

Share this post


Link to post
Share on other sites

put an invisible wall wherever you want the gfci and then put the recepticle of choice on it

  • Upvote 1

Share this post


Link to post
Share on other sites

This is just the electrician in me coming out.  The correct term is "Weather Resistant" not waterproof or weather proof. 

Weather Proof is an older term that was abandoned in the NEC about six years ago.

CA should change the symbol to WR instead of WP.

  • Upvote 1

Share this post


Link to post
Share on other sites
1 hour ago, Joe_Carrick said:

Here's a modified GFCI WR symbol.  I also rotated it so it mounts  horizontal instead of vertical.

 

GFCI WR.calibz

Thanks Joe, I save that one.

 

Share this post


Link to post
Share on other sites

Greg,

 

I just noticed that if you place a Duplex outlet (Chief's Drop Down) on an exterior Wall Chief labels it "WP". 

 

Shouldn't that always be "GFCI WR" ?

Would it ever be correct for an exterior outlet to not be GFCI protected?

 

IAE, with the new symbol I posted there's automatically a correct 2D Block that can be assigned to Chief's symbol.

Share this post


Link to post
Share on other sites
21 hours ago, Joe_Carrick said:

I just noticed that if you place a Duplex outlet (Chief's Drop Down) on an exterior Wall Chief labels it "WP". 

 

Shouldn't that always be "GFCI WR" ?

Would it ever be correct for an exterior outlet to not be GFCI protected?

 

 

Being GFCI protected and being an actual GFCI outlet are 2 different things and IMO should not be labeled the same.  I could be wrong for some areas, but I believe the GFCI label should only be placed at the location of the actual GFCI device.  If this wasn't the case, we would have all sorts of GFCI labels all over the plan anywhere and everywhere an item was on a GFCI protected circuit with no way of knowing where we actually want the device itself. 

 

Plus, the next logical step would be to carry that same thought process through to arc fault protected circuits which around here is essentially every circuit in the house now except the garage.  That's a lot of GFCI and AFCI labels cluttering the plan and honestly just confusing matters.  This is one of those areas where I feel its the electricians job to make sure circuits are properly protected.  All I want to occasionally do is specify where I might want an actual GFCI or AFCI device.  At most I think we could label the circuit itself as a GFCI/AFCI protected circuit but not each and every device on that circuit. 

 

WR outlets on the other hand are typically a different story.  Those COULD all stand to be labeled because its not a circuitry thing, its an object specific thing.  Its the device itself that needs to be weather resistant, not the circuit.

Share this post


Link to post
Share on other sites

Michael,

 

On the plans it is my opinion that all outlets should be properly labeled where protection is required.  OTOH, it's up to the Electrician to decide how to provide that protection.  Then, when installed, each protected outlet should have a physical label so indicating.

 

Share this post


Link to post
Share on other sites
34 minutes ago, Joe_Carrick said:

On the plans it is my opinion that all outlets should be properly labeled where protection is required. 

 

Ya, you are probably right and I think this is a pretty common viewpoint.  It just doesn't seem to make a whole lot of sense to me.  If you look at most electrical legends the GFCI nomenclature refers to a GFCI receptacle and not simply GFCI protection.  Of course most people dealing with the plans understand this and move on.  Then again...there are those times where GFCI receptacles get installed everywhere and I believe some localities actually require this.  

 

At any rate, answer me this...do you also include an AFCI notation at all receptacles and fixtures where AFCI protection is required?  I assume you don't and I don't blame you, but why don't you?  It seems like the same basic logic to me.  

 

Share this post


Link to post
Share on other sites
41 minutes ago, Joe_Carrick said:

Then, when installed, each protected outlet should have a physical label so indicating.

 

In my experience we are only required to do this around here when we are using a GFCI device to protect an ungrounded receptacle location that has been replaced with a grounded type receptacle .  There may be other situations requiring this as well but as far as I can recall this is the only one that has ever come up for us.  

Share this post


Link to post
Share on other sites
On 11/22/2017 at 2:45 PM, B4UBLD said:

Need help placing outdoor outlets on surfaces other than exterior structural walls.  I gather that a similar  issue has been addressed with regard to placing indoor outlets on cabinets (e.g., kitchen islands, etc.), but I do not think this is true with regard to placing waterproof GFCI outlets outdoors (e.g., on retainer walls, terrain walls, in or around outdoor kitchen areas, pergolas, etc.). However, this arises as an issue in many of my outdoor designs.   Can anyone please help me out here?.  Thanks very much in advance...

If you would be interest in a one on one online meeting (free of course), I will show you how to place anything like an outlet, fixture, etc. on anything you want. Just call me 832-754-6160 or email me at tblair55@sbcglobal.net. Happy Thanksgiving!

Share this post


Link to post
Share on other sites
10 hours ago, Alaskan_Son said:

At any rate, answer me this...do you also include an AFCI notation at all receptacles and fixtures where AFCI protection is required?  I assume you don't and I don't blame you, but why don't you?  It seems like the same basic logic to me.  

 

No, because this is done with an AFCI breaker in the panel for those circuits.  I label the circuit home runs AFCI where needed and a note in the Electrical Legend.

Share this post


Link to post
Share on other sites
19 hours ago, Joe_Carrick said:

Greg,

 

I just noticed that if you place a Duplex outlet (Chief's Drop Down) on an exterior Wall Chief labels it "WP". 

 

Shouldn't that always be "GFCI WR" ?

Would it ever be correct for an exterior outlet to not be GFCI protected?

 

IAE, with the new symbol I posted there's automatically a correct 2D Block that can be assigned to Chief's symbol.

There are a couple of exceptions in the National Electric Code.  All outside outlets must be GFCI protected except: when on a deck, more than 8 ft above ground with no access, like stairs, to the ground.  Outlets in the overhang more than 8ft above ground, dedicated to the purpose of holiday decorations.  Of course all of this can change with local codes and "the Authority Having Jurisdiction" which means the local electrical inspector.

Share this post


Link to post
Share on other sites

around here every GFCI must be labeled but not AFCI. Every exterior outlet must also be GFCI and WP.

Share this post


Link to post
Share on other sites
14 hours ago, Alaskan_Son said:

At any rate, answer me this...do you also include an AFCI notation at all receptacles and fixtures where AFCI protection is required?  I assume you don't and I don't blame you, but why don't you?  It seems like the same basic logic to me.  

 

3 hours ago, Joe_Carrick said:

No, because this is done with an AFCI breaker in the panel for those circuits.  I label the circuit home runs AFCI where needed and a note in the Electrical Legend.

 

I'm not suggesting anyone change their practices necessarily.  I'm sure much of what you guys have to draw up is based on local requirements.  I'm just trying to figure out the logic here and perhaps affect the discussion in general.

 

  • GFCI protection can also be done with a breaker just like AFCI protection can.  In those cases would you still label every outlet on the plan that is GFCI protected?  If so, why would you not do the same for the AFCI protection?
  • AFCI protection can be done with a device (receptacle) just like GFCI protection can.  What about these situations?  Do you label the home run, do you label the single device, or do you label every protected device like you do with GFCI receptacles?

I guess I still can't understand why the 2 are so commonly treated so differently.  For all intents and purposes they both work much in the same way with regard to circuit protection but they are handled completely differently with regard to plan notations.  

Share this post


Link to post
Share on other sites
On 11/22/2017 at 11:45 AM, B4UBLD said:

Need help placing outdoor outlets on surfaces other than exterior structural walls.  I gather that a similar  issue has been addressed with regard to placing indoor outlets on cabinets (e.g., kitchen islands, etc.), but I do not think this is true with regard to placing waterproof GFCI outlets outdoors (e.g., on retainer walls, terrain walls, in or around outdoor kitchen areas, pergolas, etc.). However, this arises as an issue in many of my outdoor designs.   Can anyone please help me out here?.  Thanks very much in advance...

 

Sorry for derailing your thread.  To answer your question...

 

There are quite a few ways to do this.  Joe and Ray both gave good solutions and you could take up Tommy on his offer but here are a few more solutions and tips:

  • If you use an invisible wall I think you'll have to place the outlet before changing the wall to invisible and I would probably suggest that you make that wall a No Room Definition wall as well. 
  • You can place a small cabinet onto a unique layer, mount the outlet to the cabinet, and simply turn that cabinet layer off
  • You can place an outlet onto a wall, select that outlet, click on the Open Symbol tool (little chair icon), click on the Options tab, and change it to Floor Mounted.  You can then place it wherever you want.  Might be a good idea to add this to your library for future use as well.  NOTE:  You may or may not want to adjust origin offsets and/or the CAD block but that's kind of a different subject. 

Share this post


Link to post
Share on other sites

Please sign in to comment

You will be able to leave a comment after signing in



Sign In Now

  • Member Statistics

    27478
    Total Members
    6254
    Most Online
    Oilersfan20
    Newest Member
    Oilersfan20
    Joined
  • Similar Content

    • By PrimeArch
      Hello guys. I made a custom symbols and model for my electrical because CA dont have it. 

       
      I managed to make it but the problem is  they cannot stay side by side.. they will merge  like this

       
      Btw the can stay side by side if each of em not the same height
       

       
      How do i solve this? Please help
       
    • By BuildingVision
      I have created a column out of Polyline solids and moldings.  Is there any way to get an outlet to place into this surface?  If there is not a way, what are your suggestions on what I do?  It is a dummy column framed out that surrounds a steel post, there is plenty of room for an outlet to be placed within the open interior space.  How do I place the outlet without there being a wall or a cabinet in this location?  Please see the attached image.  The red arrow points to where I would like to place an outlet.
       
      Thank you for your help!
      Nicole

    • By ChiefuserMathews
      Hi, How do I show a 3 way connection switch for a light at the top and bottom of the stair. Currently the 3 way switch can be shown only on 1 level. unless there is an another option.
      Thanks for the help
    • By lavorhaynie
      I've been an active user of Chief Architect for about 15 years now. I am currently using the X11 and have an SSA.  In all of these years using the software I have been frustrated with a couple things in the electrical area. First was the terrible placement of electrical connectors, they were never placed in a way that was visually appealing. I was always wasting time adjusting the lines after placement just to make them look nice on the plan.  Thank you Chief, in X11 the lines now, most of the time, place in a visually acceptable manner. A great time saver when doing the electrical! 
       
      The second, frustrating issue is the lack of programming to address the floor-to-floor light switching. I have over the years visited ChiefTalk hoping someone had a good solution to address this issue. I have never liked any of the proposed solutions, namely placing the correct 3-way or 4-way switch on each floor then placing cad arcs or splines to represent the electrical connector. I felt it to be a time waster and it just did not feel right using a cad line instead of an electrical connector. 
       
      So, in response to my frustration with floor-to-floor switching I came up with an idea and ran with it. I created two floor-to-floor connector symbols. The symbols are identical except that one is designated as being switched and the other is not switched.  Both are, in plan view, a 2" circle, defined as an electrical item, In 3D they are a 2" clear glass sphere and attach to the ceiling, being virtually invisible in a 3D rendering. When I am doing a floor-to-floor switch connection I place the switched symbol in the stair well then connect the switch to the symbol. The switch then automatically changes to a 3-way. I have a set of text labels that I then place over the switched symbol to indicate the usage of the switch, i.e. "To light above", etc. I have attached an X11 library containing the two floor-to-floor symbols, (switched and not switched), and the text labels I use.
       
      I hope these will save you a bit of time. Enjoy!
      LaVor
      ELEC CONNECTORS.calibz