I don't typically do wall framing plans and haven't used the auto wall framing tool before. Does anyone know why it would frame 2 corners of a rectangular building with a normal California corner, autowallframing1.thumb.png.6d51cfc36a7ea55deaaa4e19bb23f291.pngand the other two like the second image? autowallframing2.thumb.png.9157d4f2bf0cd2def863bb28607e2c7c.png

Share this post


Link to post
Share on other sites

Bug ? .....I have noticed that myself a few times , and I think I just clicked on the extra studs and deleted them...

 

 

Share this post


Link to post
Share on other sites

Thanks. Just wanted to make sure I wasn't missing something.

Sidenote: The crazy off-center non-symmetrical spacing of wall studs at the corners and around/over openings is killing me.

Share this post


Link to post
Share on other sites

Are you using X9 ?  not sure if I have seen that "bug" since I upgraded , now I think of it  , at least a test box house I just drew is the same at all 4 corners...

 

AFAIK if you put in framing reference markers/points you can set the framing layout per your needs , I don't usually as a Framer won't look at it anyway in my experience.

 

 

Share this post


Link to post
Share on other sites

This plan is in X8. I haven't downloaded X9  yet...I really need to get on that before X10 comes out. lol

 

Thanks for the tip on the framing reference points. I've already moved/aligned/centered everything on this one, but I'll check it out if I have to do a wall framing plan again. I don't do them for the same reason-framers won't even bother to look at it. 

Share this post


Link to post
Share on other sites

 

 

Not a bug, but a feature!

Try Default Settings...Framing Defaults...Wall...Miter Ends of Angled Walls...Horizontal Frame Through.

Uncheck Horizontal Frame Through.

Share this post


Link to post
Share on other sites
5 minutes ago, glennw said:

Try Default Settings...Framing Defaults...Wall...Miter Ends of Angled Walls...Horizontal Frame Through.

Uncheck Horizontal Frame Through.

Interesting - I had it unchecked, but I just tested it again and checking that box fixed it.

It also rotated all of the corners.

Thanks :)

Share this post


Link to post
Share on other sites

 

On 6/29/2017 at 9:47 PM, glennw said:

 

 

Not a bug, but a feature!

Try Default Settings...Framing Defaults...Wall...Miter Ends of Angled Walls...Horizontal Frame Through.

Uncheck Horizontal Frame Through.

 

On 6/29/2017 at 9:56 PM, mydog8it said:

Interesting - I had it unchecked, but I just tested it again and checking that box fixed it.

It also rotated all of the corners.

Thanks :)

 

Sorry guys, but I don't think thats what it is.  That setting simply changes the automated corner intersection behaviour and has nothing to do with the stud layout per se.  With that setting checked, all horizontal walls are automatically framed through like this...

Checked.thumb.jpg.24f24c656daab5e03ee2def5f8aa3eae.jpg

With the setting unchecked, all VERTICAL walls automatically frame through like this...

Unchecked.thumb.jpg.4c4ed1d662c4f6e689b57cc427521db7.jpg

 

The corner framing configuration on the other hand is MOSTLY (see note below) the result of how the layout lands.  If the layout of the last stud lands somewhere over the designated spacing (24" in this case) then you get the rotated stud...

Over.thumb.jpg.f6ae80d3d6a01659d5f7091602d19847.jpg

 

...If the layout of the last stud lands somewhere UNDER the designated stud spacing then you get a normal corner...

Under.thumb.jpg.efc3ee2fe18015a8f108fed2ae42af73.jpg

 

I'm not necessarily agreeing with the behaviour and have previously suggested some improvements in this particular area myself.  I'm just explaining how I understand it to work.

 

NOTE:  I said "MOSTLY" because the behaviour does seem to be a little inconsistent.  It does however always seem to be the result of layout landing just over or just under the set stud spacing.

  • Upvote 1

Share this post


Link to post
Share on other sites

Ahhh. So it only fixed it when I checked the box because when the corner changed directions, the stud spacing was different.  Thanks for the clarity.

 

I measured the spacing on the corners with extra studs, and sure enough, they are greater than 16" oc. Apparently I have to move and re-align everything again. 

Share this post


Link to post
Share on other sites

Now this has me wondering - is the "frame through" typically on the load bearing walls?

Like this (cross hatch is bearing): autowallframing1.thumb.png.6d51cfc36a7ea55deaaa4e19bb23f291.png

 

Share this post


Link to post
Share on other sites

I thought I remembered the "bug" in X7 and X8 with Corners of each kind on opposite ends of the Building/wall but not since I upgraded to X9 but I may not have been looking often enough to notice? 

 

  yep spoke too soon , must have got lucky earlier? I  just did a 2nd test house with frame through enabled per Glenn's comment and I have different framing at each end which I am thinking is caused by the direction the wall is drawn in? ie usually Clockwise around the house, however I am not sure what CA's default layout is guided by?

 

 

Capture1.JPG

Share this post


Link to post
Share on other sites

Michael,

 

Yes, I basically agree with what you are saying.

But...

3 hours ago, Alaskan_Son said:

If the layout of the last stud lands somewhere UNDER the designated stud spacing then you get a normal corner

I believe this is incorrect though.

PS - I could be misinterpreting what you are saying here - if so, ignore.

I think the U shaped studs occur when a wall perpendicular to the "through wall" sit over a stud in the "through wall" - even if it is under the stud spacing.

The "frame through" setting - either horizontal or vertical effects which walls get the U shaped stud arrangement.

 

It is only the "frame through" walls that can have the U shaped stud arrangement.

This can either be set in the wall framing defaults or on a wall by wall and wall end basis. (see below).


 

Quote

 

 I have different framing at each end which I am thinking is caused by the direction the wall is drawn in? ie usually Clockwise around the house, however I am not sure what CA's default layout is guided by

 

I think this only happens for 1 of 2 reasons:

1. When the "frame through" wall is sitting directly over where a stud in the perpendicular wall would be - happens sometimes.

or, more likely when

2. the Through Wall at Start or Through Wall at End have been used on an individual wall by wall and wall end basis.

This setting in individual walls will override the default setting in the Framing Defaults.

Obviously reversing the wall direction will influence the framing if either of the above settings are used.

 

By using some or all of these settings, you should be able to control the arrangement of studs in any corner.

 

Make sure auto wall framing is on before trying any of this.

 

If I could get Jing working, I would do a video.

 

Share this post


Link to post
Share on other sites

All I know is that Chief has needed to work on framing for a long time now, it's time for X10 please.

  • Upvote 2

Share this post


Link to post
Share on other sites

So, as far as best practice when actually framing the building, there would be a typical 3-stud California corner on each corner (without the "u" CA is adding), and the "frame though" would be on the bearing wall? I'd love feedback from any contractors on how this is actually done vs. rendered.

Share this post


Link to post
Share on other sites

I would personally want to see 4 things at an exterior corner like that...

 

1.  A stud that lands ON LAYOUT for exterior sheathing and siding reasons as well as to provide proper bearing in some circumstances.

 

2.  Drywall backing.

 

3.  Something to tie the corner together in such a way that limits movement and therefore potential drywall cracks or screw pops in the future.  

 

4.  A little less important, but access for insulation and wiring purposes.  

 

There are a good handful of alternative methods, but in my opinion Chief has chosen what I feel is the single best compromise with that rotated end stud.  

Share this post


Link to post
Share on other sites
9 minutes ago, Alaskan_Son said:

I would personally want to see 4 things at an exterior corner like that...

 

1.  A stud that lands ON LAYOUT for exterior sheathing and siding reasons as well as to provide proper bearing in some circumstances.

 

2.  Drywall backing.

 

3.  Something to tie the corner together in such a way that limits movement and therefore potential drywall cracks or screw pops in the future.  

 

4.  A little less important, but access for insulation and wiring purposes.  

 

There are a good handful of alternative methods, but in my opinion Chief has chosen what I feel is the single best compromise with that rotated end stud.  

Thanks for the feedback! When you say "on layout," do you mean a stud at each edge of the shear panel?

Share this post


Link to post
Share on other sites
1 hour ago, mydog8it said:

Thanks for the feedback! When you say "on layout," do you mean a stud at each edge of the shear panel?

 

Yes and no.  The edge of the shear panel is where I would consider it to be most important, but it's really just the spacing in general that I'm referring to.  If for example we are framing at 24" on center, I want to have a stud at every 24" increment no matter what.  I will personally very rarely shift stud spacing for anything.  If there is no stud on layout it can cause problems for insulation, wall sheathing, wall coverings, siding, trim, and all sorts of other things. 

Share this post


Link to post
Share on other sites

Here is the video.

I ran out of time with the 5 minute limit, but you can get the jist of it.

I forgot to mention that you can obviously only get the U shaped framing in a Frame Through wall.

 

https://www.screencast.com/t/B5IaHCRA7Kv

 

 

Share this post


Link to post
Share on other sites

Around here edges of shear walls require a 4x4 post or 4x6 if 2x6 studs, even in the corners. I add them manually.

Share this post


Link to post
Share on other sites
7 hours ago, glennw said:

Here is the video.

I ran out of time with the 5 minute limit, but you can get the jist of it.

I forgot to mention that you can obviously only get the U shaped framing in a Frame Through wall.

 

https://www.screencast.com/t/B5IaHCRA7Kv

 

 

 

Thanks for the video Glenn , that cleared things up for me a bit better on what was happening.

 

@mydog8it

  typically around here we now use 3 stud corners due to the insulation requirements and

no U framing at Partition walls either for the same reason , just a 2x6 or 2x8 on the flat, though

I usually add a stud to Partition wall backing to stiffen so it is L shaped, and leave my layout standard.

Share this post


Link to post
Share on other sites
11 hours ago, Alaskan_Son said:

 

Yes and no.  The edge of the shear panel is where I would consider it to be most important, but it's really just the spacing in general that I'm referring to.  If for example we are framing at 24" on center, I want to have a stud at every 24" increment no matter what.  I will personally very rarely shift stud spacing for anything.  If there is no stud on layout it can cause problems for insulation, wall sheathing, wall coverings, siding, trim, and all sorts of other things. 

Got it. This is super helpful. Thank you!

 

31 minutes ago, Kbird1 said:

 

Thanks for the video Glenn , that cleared things up for me a bit better on what was happening.

 

@mydog8it

  typically around here we now use 3 stud corners due to the insulation requirements and

no U framing at Partition walls either for the same reason , just a 2x6 or 2x8 on the flat, though

I usually add a stud to Partition wall backing to stiffen so it is L shaped, and leave my layout standard.

Thanks- I was wondering about the partition walls, too. 

 

8 hours ago, glennw said:

Here is the video.

I ran out of time with the 5 minute limit, but you can get the jist of it.

I forgot to mention that you can obviously only get the U shaped framing in a Frame Through wall.

 

https://www.screencast.com/t/B5IaHCRA7Kv

 

 

Can't watch on my phone, but i will check this out when I'm at my desk :)

 

1 hour ago, DRAWZILLA said:

Around here edges of shear walls require a 4x4 post or 4x6 if 2x6 studs, even in the corners. I add them manually.

Interesting. 

Share this post


Link to post
Share on other sites

Please sign in to comment

You will be able to leave a comment after signing in



Sign In Now

  • Member Statistics

    27450
    Total Members
    6254
    Most Online
    Elliot
    Newest Member
    Elliot
    Joined
  • Similar Content

    • By 9atatimer
      I'm using X11 premier on a mac -- I have an exterior garage wall (with a centered garage door) and a gable end -- I'd like to split the attic wall of the gable end into 3 parts -- the central region above the garage door, and the left and right, to have a different material above the garage door.

      I have Default Settings > Roof > Auto Rebuild Roof set to Off
      I have Default Settings > Framing > Automatically Build Floor and Ceiling Framing Off on all framing types.
      I have Default Settings > Walls > General Walls > Auto Rebuild Attic Walls set to Off

      If I delete the roof and ceiling planes with Build > Roof > Delete [X] and then use the Build > Roof > Build Roof ... dialog to rebuild the roof and attic from scratch -- I leave the Auto Rebuild Roofs set to Off, to be clear -- and then edit the resulting gable roof on the attic layer, I can split it twice to produce the three separate wall sections, but once I change the exterior material on any of the sections, the three wall segments get replaced with a single wall again.  The new wall has my selected material, but that does me no good as I need the distinct secgments.

      Anyone know what setting do I need to turn off to maintain the manually edited gable end?  Or is this a mac bug?

      Or, barring that, does anyone know what approach will let me give the desired finish detail (attached a pic of a freehand elevation)?

    • By KirkHodgson
      I'm looking to make my retaing wall larger than the terrain heights.
      In the instructions in this page, https://www.chiefarchitect.com/support/article/KB-00652/changing-the-height-of-a-retaining-wall.html
      I did all the steps, but the last point. In section/elevation, when I try to click the retaining walls, nothing happens. I don't get boxes or any selection at all.
      What is happening that I can't make this selection?
      I want to make my wall 6" above the grade/terrain elevation, and I want to drop the foundation of the wall by 24". How do I do this?
       
      Please assist.
      Thank you.
       

    • By MRMChief
      Happy Holidays everyone.
       
      I have a plan where I have a few places I need an exterior wall above a roof section, but a railing, or in one case, no wall below.  Is there a way to do this in Chief Architect X11?  The one opening in my screen shot shows some exterior molding, but no wall.  On the one that has the railing below it, I tried the lower wall type if split by roof, but I couldn't get it to show as a wall above and a railing below.  It was either only a railing or all wall.
       
      I am on a macbook pro..
       
      Thanks,

      Michael


    • By mprovost129
      Hi all. I'm fairly new to the software and have only been using it since October. I have a client who wants a wood framed chimney extruding from the middle of the roof up from the gas fireplace. I've tried a bunch of different options to make this work but can't figure it out. Can someone please tell me how to draw walls on top of the roof?
       
      Thank you!
       

    • By Designer100
      In 3d there is a wall sticking out. see jpeg attached. I cannot figure it out to remove.
      NEW-William_Dowdell_Dr.plan