Hello all, 

I am a former user of AutoCad and also of Turbo CAD. I finally made the switch to Chief Architect Premier X9 about a month ago. I decided to start the switch with a fairly simple plan. I also recently purchased "Residential Design Using Chief Architect X9" by Terry Munson last week. Although this book has been helpful I still haven't found what I'm looking for. I am trying to create a floating slab foundation that is common in Southwest Oklahoma. I believe IRC refers to them as ground supported slabs. I have a screen shot of one of the details that was created in a previous CAD program. I have also attached the plan in question. All I can seem to manage is a monolithic slab which is used in some localities, but not where this home will be built. Any help is greatly appreciated.

FOUNDATION SECTION.JPG

Share this post


Link to post
Share on other sites

OK follow up question, I am unable to upload the plan file so maybe I should begin with asking how to accomplish this? The file size is 18.3 MB but the forum is blocking it. Any suggestions?

Share this post


Link to post
Share on other sites

You can zip the file - some may want to help you right in your file, but what you provided as an example is generic enough in my opinion to get help on.

Share this post


Link to post
Share on other sites

Change the default foundation wall. 8" with the size footing you need.

 

Check Hang Floor Structure Inside Foundation Wall (in the build foundation dialog).

 

Edit the default 1st floor, floor structure making it a slab.

 

Build the foundation.

 

I had to change the stem wall height manually, making it shorter.

 

Here is the plan. I'm sure I left something out, so ask if it's not working for you.

 

OK 1.plan

 

 

Share this post


Link to post
Share on other sites

Here's another method:

1. Replace the interior grade beams with Slabs, and put them on the Footings layer:

1.thumb.PNG.8f40ea30110939f388e7906a4a10cf6d.PNG1a.thumb.PNG.267bda80b56dc74f369dc2f033b8a2c3.PNG1b.thumb.PNG.cdcfa2ba9a9fe6f447a515586fe2c57e.PNG

 

2. Select the Level 0 room and set the Stem Wall (I) value to 16". (You already have the other two critical settings correct: Floor>Room Supplies Floor for the Room Above, and Floor Structure (L) set to 4"):

2.thumb.PNG.df00f784e5bf7fe5e9afb3c605d7a191.PNG

 

3. Select all four Foundation Walls and set the Foundation>Footing values to 16"x20". Also uncheck Center Footing on Main Layer so you can set the Footing Offset to -1":

3.thumb.PNG.4a8ea6504b6cb7a99fbe07b1b17e858d.PNG

 

These few setting should give you what you're looking for: 1703plan-6.plan

4.thumb.PNG.95b785815a783fc44267322854d87f75.PNG

Share this post


Link to post
Share on other sites

I think the best method is to ZERO OUT floor assembly at LEVEL 1 and then put the SLAB ON LEVEL 0.

 

Using this method,

 you can control elevation of the slab independent of everything else on level 0 or level 1

you can control height of conc stem wall independent of everything else on level 0 or level 1

you can control the width of all footings separately but of course the top of footing will be a constant for all stem walls.

 

give it a try.  No manually adjusting height of stem walls.

 

 

 

  • Upvote 1

Share this post


Link to post
Share on other sites
1 minute ago, dshall said:

I think the best method is to ZERO OUT floor assembly at LEVEL 1 and then put the SLAB ON LEVEL 0.

 

Doesn't Room Supplies Floor for the Room Above accomplish this? It allows independent control of the slab elevation using the Level 0 structure dbx, control of the stem wall height in the Level 0 structure dbx, and the width of footings in the wall dbx.

Share this post


Link to post
Share on other sites
1 hour ago, rlackore said:

 

Doesn't Room Supplies Floor for the Room Above accomplish this? It allows independent control of the slab elevation using the Level 0 structure dbx, control of the stem wall height in the Level 0 structure dbx, and the width of footings in the wall dbx.

 

Yep,  I guess so,  I did that the first time and it seemed like I had less control.  

Share this post


Link to post
Share on other sites

of course you still need a cad detail for rebar and exact condition, Chief doesn't do that.

Share this post


Link to post
Share on other sites
1 minute ago, DRAWZILLA said:

of course you still need a cad detail for rebar and exact condition, Chief doesn't do that.

 

You know, that's a good point. We can specify a lot of the rebar conditions in the Foundation Defaults>Options dbx. It wouldn't take much more for Chief to expand that tab of the dbx a bit, then include the rebar in the Auto Detail tool.

Share this post


Link to post
Share on other sites

Yes, that would be great, if possible.

Share this post


Link to post
Share on other sites

It's gonna take some manual work to get that dropped slope bottom slab edge, right?  P-line solids, get everything on right levels, white-out joint line in section view, yadda yadda yadda.

 

Unless there's a trick I don't know.

Share this post


Link to post
Share on other sites
9 minutes ago, GeneDavis said:

It's gonna take some manual work to get that dropped slope bottom slab edge, right?

 

Gene, that's the gravel base, not the slab.

Share this post


Link to post
Share on other sites

Thanks, Robert.  Took to quick a look at the OP's detail.

Share this post


Link to post
Share on other sites

I know it's late, and I am really burning the midnight oil on this project. I tried each of these suggestions and worked on each to try to understand what is exactly happening. Solver's suggestion to "Check Hang Floor Structure Inside Foundation Wall (in the build foundation dialog)" was a useful key to understand why I couldn't get the slab inside of the stem wall as I need. rlackore's suggestion looks correct, and I really appreciate uploading the plan file so that I can see what you did. I'm not sure I fully understand what's happening there though. I think it must be a little advanced for me just yet.

 

Again, bravo and thank each of you for the help. I'm taking the plunge and using a client with a simple form home and a long deadline to learn the new software. 

Share this post


Link to post
Share on other sites

Did you get things to work for you?

Share this post


Link to post
Share on other sites

An advantage to building the slab on level 0  and not on level 1  (not using floor supplied by floor below) .....  is you can auto put a sill plate on the foundation stem wall and still get a sill plate for the wall.  I usually do not build it this way,  but it is an option if you want the additional sill plate.

 

 

5936b824d87c3_ScreenShot2017-06-06at7_08_49AM.thumb.png.a55f1ec29851bb3219a46f417ff14f18.png

 

  • Upvote 1

Share this post


Link to post
Share on other sites
13 minutes ago, dshall said:

An advantage to building the slab on level 0  and not on level 1  (not using floor supplied by floor below) .....  is you can auto put a sill plate on the foundation stem wall and still get a sill plate for the wall.  I usually do not build it this way,  but it is an option if you want the additional sill plate.

 

 

5936b824d87c3_ScreenShot2017-06-06at7_08_49AM.thumb.png.a55f1ec29851bb3219a46f417ff14f18.png

 

Good point, Scott. Your example is exactly the way we build garages here. Almost all of the designs I do are on crawlspaces or basements for the main house. However, slabs are becoming more popular, mainly on "Barndominiums."

Share this post


Link to post
Share on other sites
36 minutes ago, dshall said:

An advantage to building the slab on level 0  and not on level 1  (not using floor supplied by floor below) .....  is you can auto put a sill plate on the foundation stem wall and still get a sill plate for the wall.  I usually do not build it this way,  but it is an option if you want the additional sill plate.

 

 

5936b824d87c3_ScreenShot2017-06-06at7_08_49AM.thumb.png.a55f1ec29851bb3219a46f417ff14f18.png

 

 

What's the construction advantage to double-plating this condition? I'm not arguing, I'm curious.

Share this post


Link to post
Share on other sites

Double sill plates help if the foundation is out of level... you can shim between plates to make it right.

Share this post


Link to post
Share on other sites
45 minutes ago, rlackore said:

 

What's the construction advantage to double-plating this condition? I'm not arguing, I'm curious.

 

I for one always frame that way for the sake of framing efficiency.  In order to frame and sheath that wall while it is lying down, you need a bottom plate.  In addition to the issue Parkwest mentions above the problem with using the 2x8 sill as the bottom plate is 2 fold...

  1. Tipping it up onto the anchor bolts is a huge pain.  Not only do the bolts themselves get in the way and hang up the wall while it is getting stood up, but they can also be very difficult to line up after the wall is stood up.  The fact the wall has to be up above the anchor bolts in order to slide down over the top of them also makes doing it this way a lot more dangerous as the bottom of the wall has to be pretty well completely disconnected from anything while performing this part of the operation.  I won't go into all the details and problems involved but suffice it to say that it can really be a messy pain.
  2. In order to frame the wall properly and to tip it up in the safest and most effective manner, the bottom of the 2x8 bottom plate would need to be lined up with the inside of the foundation wall.    This gives a person no really good place to pop a straight line or to temporarily fasten that bottom plate in order to ensure the bottom is straight and secure before sheathing and standing it. 

If the 2x8 sill is installed first, most all of the problems are reduced or completely eliminated.  Actually, about 12 years ago I started adding one extra step.  I would install the sill plate, tighten down all the nuts, and then I would run around with a cut off tool and cut off all the excess anchor bolt.  I would then install some 3/4" plywood or common pine strips that ran from nut to nut.  This would completely eliminate the need to drill out and line up the bottom plate of the wall.  It also had the advantage of allowing us to use standard studs and even build a single continuous wall between the living space and garage if we were building a zero entry foundation.

 

Anyway, there are just a few reasons why the multiple plates can be a good thing.

Share this post


Link to post
Share on other sites

Please sign in to comment

You will be able to leave a comment after signing in



Sign In Now

  • Member Statistics

    27996
    Total Members
    6254
    Most Online
    MAP6933
    Newest Member
    MAP6933
    Joined
  • Similar Content

    • By Designer100
      Is there a way to add pre Mfg. brick to outside of the foundation above grade that does not affect the porches etc or parts you do not want it?
       
      Newell Cheatheam
      www.newellsdesigns.com
      newell.cheatheam@gmail.com
      x11 
    • By DRyeHD
      I've looked for a thread on this topic but cannot find one.  Typical construction is CMU stem wall on footing and slab.
       
      I would like to show outside edge of foundation block and all thickened slab areas (for bearing walls and posts).  I see the foundation block on floor "0" and the thickened slab (under bearing walls) and post footings on floor "1".  I would like to display all this on one layout and add dimensions for concrete, plumbing, and other under-slab work.
       
      What is the best way to do this without redrawing a separate plan to accommodate these items?
    • By CRHDesign
      Is there a room dialog to prevent this from happening? Ideally I want to make the cantilever a "cantilever" room and have it not generate walls under the cantilever with auto rebuild foundation walls on. Unless there is an easier way? Copying the balcony room settings ends up generating walls like the attached picture, still generating walls under cantilever. Feel like I'm missing something very simple.
    • By Designer100
      I cannot get the floor joists to  build.It originally a regular slab home.  but now it is pier and  beam with concrete  block around preiemerter at 8' o.c. or wha ever engineer specs out.  I cannot the the floor joist to build on first floor, cannot garage to show 4" drop with preimerter  walls and regular lab,garage left wall to close in. Rear deck will not show up in rendering either.
      FFE 61.00, top of cmu  blocks 60.00, existing grade 57.30', top of grade beam 57.33. garagefloor 52.33 8 cmu blocks abovegarage slab.perfer 12" all around outside of garage foundation. 
       
       
      I would appreciate getting the first floor joists to be installed. and the other issues.
      Plan 5661LAF.GARAGE.PIER&BM.zip



    • By JimAlsup
      Hello All,
       
      I'm trying to figure out the best way to do the foundation for an addition to our 1955 home.  The existing home crawl space is minimal.  Perimeter stem wall is 18 inches with 4/6 girders resting on the sill and footings/posts at 4' O.C. .  Flooring is 2x6 T&G floor boards resting on the girders.  Not sure if that meets modern code. 
       
      For the new foundation area I was thinking of using 2x8 joists for the floor framing and matching the existing stem wall.  I cannot use wider joist without raising the floor as I cannot lower the stem wall height due to code requiring 8" min stem top to group level.  The addition needs to span distances beyond the 12' span distance so I need to support them in some way.  Girders with posts seems reasonable, but I'm concerned about the crawl space height.   2x8 joists on 18" 16" O.C is tighter than the existing foundation which has 18+5.5 and widely spaced girders dropping it to 18".  The new foundation with 4x8 joists at 16" on center and girders would drop the bottom the height to 12" under the beams which seems very tight.  I think the code allows for 12", but is it bad practice?  Am I wasting my time worrying about this? 
       
      I have a few ideas on increasing the clearance, but I don't know which would work best and what the cost trade offs are?
       
      1. Move the 4x6 girder to foundation stem wall height and then attach joists with joist hangers rather than resting on top.
      2. Build internal foundation footing/stem walls as needed to close 2x8 spans to 12' or less (leave access openings)
      3. If legal, copy the existing floor structure.  I'm guessing the 4/6 girders and T&G flooring is likely more costly.
      4. Extend the addition's stem wall and interior ground level down 6 inches.  Slope the soil away from the existing foundation 2" a foot. Excavation and concrete costs go up.
       
      Thoughts?
       
      Thank you,,
      Jim