Joe_Carrick

Electrical Panel Location ?

Recommended Posts

I know we can't per ( CRC, IRC } put an Electrical Panel in a Bathroom but what about a Laundry Room?

Is it allowed?

I know I did it in a remodel project about 10 years ago in San Diego but that was when the codes and plan check requirements were much easier.;)

 

Share this post


Link to post
Share on other sites

I'm actually going through this right now in North Carolina. Bathrooms and tight areas such as closets or small storage room areas will get turned down here. Laundry rooms are OK if the room is big enough and you can easily access the panel. Meaning you can't put the panel behind the washer and dryer even if they are on the floor and especially if they are stacked on-top of each other. Other then that just the basics of no higher then 6'-7" off the floor, well lite, and min. 3 ft square clear from walls.

 

To be safe I like to put the panel on the opposite wall as the washer and dryer but as long as you can fully stand in front of the panel it is OK to be on the same or adjacent wall.

Share this post


Link to post
Share on other sites

I believe it can be in a laundry room. What is the issue is the clearance for working space. I think it is 15" clear each side of panel and min 36" behind.

Share this post


Link to post
Share on other sites

  Sec. 110-26 of the National Electrical Code (NEC): 1) at least a 3-ft clearance in front of all electrical equipment; 2) a 30 in.-wide working space in front of equipment operating at 600V or less; and 3) minimum headroom clearance of 6 ft or the height of the equipment, whichever is greater.

Share this post


Link to post
Share on other sites
1 hour ago, 2wheeltodd said:

  Sec. 110-26 of the National Electrical Code (NEC): 1) at least a 3-ft clearance in front of all electrical equipment; 2) a 30 in.-wide working space in front of equipment operating at 600V or less; and 3) minimum headroom clearance of 6 ft or the height of the equipment, whichever is greater.

for reference, from the 2016 CEC, highlighting is from the adoption table and nothing to do with this topic

5afa0453be1a5_PanelClearance1of3.thumb.PNG.8b8d6cc7c6c021c7531dafd2c670f654.PNG5afa0454d6b8f_PanelClearance2of3.thumb.PNG.4e2c72b388990fcb4f58702dfa87102d.PNG

Share this post


Link to post
Share on other sites

It's probably late, but, for the future, for those under PG&E look up the Greenbook under "prohibited locations" it specifies where not to put an electrical panel.

Share this post


Link to post
Share on other sites
On 5/14/2018 at 1:38 PM, 2wheeltodd said:

  Sec. 110-26 of the National Electrical Code (NEC): 1) at least a 3-ft clearance in front of all electrical equipment; 2) a 30 in.-wide working space in front of equipment operating at 600V or less; and 3) minimum headroom clearance of 6 ft or the height of the equipment, whichever is greater.

At least here, it is good to know that the 30" wide space need not be centered on the panel, but the the panel must be within the 30".

Share this post


Link to post
Share on other sites