1 hr fire rated detail- one side only


RL-inc
 Share

Recommended Posts

I have a buddy that is building a steel warehouse and he needs a 1hr fire rated assembly along the rear wall line due to proximity to PL.

Typ. steel building with no sheathing on the exterior side .

He does have 5/8" type X on the interior but I can't find a 1hr detail showing only that material on one side-

Anyone ever see a similar condition of have a supporting detail?

 

Much appreciated as always

Link to comment
Share on other sites

I will look at the drawings when I check the job this afternoon-

If it is required from both sides the building design the had approved would not have met that standard however-

That said, I am assuming that the rating is from the interior side only.

Link to comment
Share on other sites

Check out the UL BXUV V421 assembly. If you don't have access to the online UL database, you can use the attached publication from the MBMA - it's old, but the assembly hasn't changed. The head-of-wall is an area of special concern - you'll have to detail that yourself based on the roof construction.

 

MBMA UL V421.pdf

 

 

Link to comment
Share on other sites