RL-inc Posted May 10, 2021 Share Posted May 10, 2021 I have a buddy that is building a steel warehouse and he needs a 1hr fire rated assembly along the rear wall line due to proximity to PL. Typ. steel building with no sheathing on the exterior side . He does have 5/8" type X on the interior but I can't find a 1hr detail showing only that material on one side- Anyone ever see a similar condition of have a supporting detail? Much appreciated as always Link to comment Share on other sites More sharing options...
rlackore Posted May 10, 2021 Share Posted May 10, 2021 Does the fire separation distance require a wall rated from both sides, or just the interior side? Link to comment Share on other sites More sharing options...
RL-inc Posted May 10, 2021 Author Share Posted May 10, 2021 I will look at the drawings when I check the job this afternoon- If it is required from both sides the building design the had approved would not have met that standard however- That said, I am assuming that the rating is from the interior side only. Link to comment Share on other sites More sharing options...
rlackore Posted May 10, 2021 Share Posted May 10, 2021 Check out the UL BXUV V421 assembly. If you don't have access to the online UL database, you can use the attached publication from the MBMA - it's old, but the assembly hasn't changed. The head-of-wall is an area of special concern - you'll have to detail that yourself based on the roof construction. MBMA UL V421.pdf Link to comment Share on other sites More sharing options...
RL-inc Posted May 10, 2021 Author Share Posted May 10, 2021 Thanks Robert- Looks like the min I can find for a one side only application is 3 layers of 5/8" type X per WP9021. Better run with what we have spec'd! Link to comment Share on other sites More sharing options...
rlackore Posted May 10, 2021 Share Posted May 10, 2021 The Gypsum Association WP 9021 requires 3 layers of 5/8" type X, but the UL V421 allows 3 layers of 1/2" regular. The UL assembly might save a bit of money, if the building department allows the UL assembly. Link to comment Share on other sites More sharing options...